Has anyone tried one of these or think its a good/bad idea to give it a try?
 
#13 ·
Yea that's fine.. DC coils don't even have surge current so they are equal (surge and hold amp draw). AC is different..
for AC 2x "hold" would suffice in most cases...

YMMV
Current in a dc solenoid depends only on resistance, so inrush and holding current are no different. This is why the MOPD rating is lower with direct current; there is no benefit of initial over-current to assist in lifting the plunger.

Recently, electronically enhanced dc coils have been developed which artificially produce an over-current for the first few milliseconds, simulating the inrush current of ac and providing full MOPD.
http://www.achrnews.com/articles/solenoid-valves-operation-selection-and-application