Aquarium Placement in Concrete Condo Building

Hi,

I know this type of question gets asked often, but I don't often see information for highrise buildings with reinforced concrete slab floors.

I will be moving into a concrete condo that will be completed next year and I am thinking about getting an aquarium.

The developer says the floors are 8" thick concrete and are designed for a liveload of 40psf. I think that means that a 10'x10' room can safely support a uniformly distributed load of 4000lbs.

The aquarium I am looking at would weigh about 600lbs including stand, equipment, contents etc. I would like to place it against an interior wall (not load bearing). Based on drawings I've been given, the nearest concrete pillar is about 8ft away from the centre of the aquarium.

I realize strength wise the floor will have no problems supporting 600lbs.

However, I do wonder about the deflection and sag in the floor over time since the aquarium will be there for years.

Does anyone have thoughts on this? Any structural/civil engineers?

Thanks!
Spit1A is offline  
Sponsored Links
Advertisement
 
post #2 of 17 (permalink) Old 11-04-2015, 04:38 PM
Algae Grower
 
PTrader: (0/0%)
Join Date: Dec 2014
Location: Maine
Posts: 55
What are the dimensions of the tank, and how far is the second closest pillar (in the other direction)?
Measle is offline  
post #3 of 17 (permalink) Old 11-04-2015, 05:05 PM Thread Starter
Algae Grower
 
PTrader: (0/0%)
Join Date: May 2014
Location: BC, Canada
Posts: 54
Quote:
Originally Posted by Measle View Post
What are the dimensions of the tank, and how far is the second closest pillar (in the other direction)?
The foot print of the tank would be about 30"x18". I would put it on a stand that distributes the weight evenly.

The second closest pillar is approximately 12ft away.
Spit1A is offline  
 
post #4 of 17 (permalink) Old 11-04-2015, 05:14 PM
Algae Grower
 
PTrader: (0/0%)
Join Date: Dec 2014
Location: Maine
Posts: 55
That would be a surface area of 3.75 sq.ft. I've only taken an architecture class, that's as far as my experience takes me hahaha. Though 40 pounds per foot seems a little low. Knowing how much rebar is in the floor could make a difference though.
Measle is offline  
post #5 of 17 (permalink) Old 11-04-2015, 05:16 PM
Wannabe Guru
 
PTrader: (0/0%)
Join Date: Jun 2014
Location: Cape Coral, Florida
Posts: 1,286
I think you are worrying much too much. 600 pounds is nothing, your fat buddy from college can stop by, jump up and down and generate more load.

8" of reinforced concrete distributes load very effectively.

Another way to think of it is that the concrete itself on a 10'x10'x8" slab weighs in just shy of 10,000 pounds, not including the rebarb. Your little tank is 6% of the load it is carrying already.

House floors are much more problematic as, especially as they age and get homeowner work done, in that they may have weak spots, little more than a thin sheet of plywood. Put a tank so it sits between supports on it and ... splash.

But reinforced concrete... I just wouldn't worry about a 600 pound tank.

I WOULD worry that you are covered for leaks or floods that ruin your downstairs neighbor's leopard skin carpet. Concrete is strong but rarely waterproof. Mistakes and aquariums go together better than peanut butter and jelly.
tuffgong, tuffgong, Spit1A and 1 others like this.

Linwood

Latest tank build:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Linwood is offline  
post #6 of 17 (permalink) Old 11-04-2015, 06:36 PM
Planted Tank Enthusiast
 
tomfromstlouis's Avatar
 
PTrader: (13/100%)
Join Date: Apr 2012
Location: Saint Louis
Posts: 802
I keep a 220g with a 6' x 2' footprint in a concrete slab high rise. The only issue was when it leaked to the eighth floor.

Concrete does not deflect much so nearness to columns would not concern me. My father was a structural engineer and we discussed this back in the day.

RAOK Club #76

220g altum, 75g high tech, 6g shrimp: one office, three tanks
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
tomfromstlouis is offline  
post #7 of 17 (permalink) Old 11-04-2015, 07:16 PM
Wannabe Guru
 
lksdrinker's Avatar
 
PTrader: (9/100%)
Join Date: Feb 2014
Location: NY; LETS GO METS
Posts: 1,916
You're probably making a mountain out of a mole hill here. What size tank is this (in gallons?) A footprint of 30x18 footprint is not all that large of a tank (unless its really, really tall), so chances are that 600 pound figure you're using is a big overestimate. But, better to do this kind of figuring using the largest numbers possible. Would you worry about having 3 or 4 full grown men standing very close to one another in the house?

Also worth noting that the 40 psf liveload is probably a conservative estimate as there is a safety factor worked in there as well. Meaning the failure of the floor probably wont be seen until more than twice the liveload is applied. the 40 psf is also essentially the average across the whole floor . The actual number likely changes dramatically based on where the support columns are as well as the various other structural elements.

As far as sag or deflection; i dont think you have much to worry about with an 8" concrete slab.

A lot of good info regarding this kind of information as it relates specifically to the aquarium hobby can be found here: http://www.african-cichlid.com/Structure.htm
lksdrinker is offline  
post #8 of 17 (permalink) Old 11-04-2015, 10:17 PM
Planted Tank Guru
 
PlantedRich's Avatar
 
PTrader: (2/100%)
Join Date: Jul 2010
Location: United States
Posts: 12,121
Something major wrong with the numbers? A floor that supports 40 pounds per square foot? How much does a 200 pound guy put on the floor when he stands on one foot? Most buildings have proven to hold a guy that size!
New concrete buildings will hold far more than the tank.
If the building can't hold two fat people setting on a couch--- don't move there!
PlantedRich is offline  
post #9 of 17 (permalink) Old 11-04-2015, 10:37 PM Thread Starter
Algae Grower
 
PTrader: (0/0%)
Join Date: May 2014
Location: BC, Canada
Posts: 54
Quote:
Originally Posted by PlantedRich View Post
Something major wrong with the numbers? A floor that supports 40 pounds per square foot?...
I think 40psf is a standard rating for residential buildings. It just means that the floor can support 40psf of pressure over the entire floor. So a 10'x10' room could support 4000lbs if it was distributed evenly. But in reality loads are more concentrated.

Quote:
Originally Posted by lksdrinker View Post
You're probably making a mountain out of a mole hill here. What size tank is this (in gallons?) A footprint of 30x18 footprint is not all that large of a tank (unless its really, really tall), so chances are that 600 pound figure you're using is a big overestimate.
Yea I'm thinking of a 30 to 40 gal tank. I added weight for a sturdy stand, hardscape, equipment and a fudge factor. So yes, 600lbs is an overestimate.

Thanks for the comments and the reference link! I guess I'm just being over worried.
Spit1A is offline  
post #10 of 17 (permalink) Old 11-04-2015, 10:40 PM
Wannabe Guru
 
PTrader: (0/0%)
Join Date: Jun 2014
Location: Cape Coral, Florida
Posts: 1,286
Quote:
Originally Posted by Spit1A View Post
I guess I'm just being over worried.
Always better than the opposite.

Linwood

Latest tank build:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Linwood is offline  
post #11 of 17 (permalink) Old 11-05-2015, 12:26 AM
Planted Tank Guru
 
PlantedRich's Avatar
 
PTrader: (2/100%)
Join Date: Jul 2010
Location: United States
Posts: 12,121
40PSF is standard for WOOD floors but new concrete is normally much stronger. It also gets much more complex to figure but even at worst a floor should easily support two large linemen standing sideby in a closet!
2X6 closet=12SF X 40= 480pounds so the lineman can only weigh 240 each to be safe? Not very realistic numbers are they? Heaven help the pro QB that invites the line over for a steak dinner!!

But the point for most of us is that it really is not a problem. There are many larger tanks in far worse buildings and we never drop them through the floor. Sleep well and go for it with a clear mind.
Spit1A and Spit1A like this.
PlantedRich is offline  
post #12 of 17 (permalink) Old 11-05-2015, 12:29 AM
Wannabe Guru
 
PTrader: (0/0%)
Join Date: Jun 2014
Location: Cape Coral, Florida
Posts: 1,286
Quote:
Originally Posted by PlantedRich View Post
Heaven help the pro QB that invites the line over for a steak dinner!!
Well, it depends on how big their shoes are. If they have really big feet it spreads the load out.

There is a little known NFL guideline, however, that when dining together on an upper floor, they are not allowed to wear high, stiletto heels. This concentrates the weight too much.

If you watch social events carefully, you will see all teams carefully abide by this guideline.

Spit1A and Spit1A like this.

Linwood

Latest tank build:
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Linwood is offline  
post #13 of 17 (permalink) Old 11-06-2015, 02:35 PM
Planted Tank Guru
 
Zorfox's Avatar
 
PTrader: (5/100%)
Join Date: Jun 2012
Location: Gainesville, FL
Posts: 2,105
The 40psf is the minimum requirement for residential live loads. I doubt that's the actual calculated live load for your floor merely a minimum specified limitation. A mobile home has to have a live load of at least 40psf.

I agree with Linwood. Don't worry about the weight instead what happens when it leaks. You may want to check with the condo association. Many condo associations require insurance on aquariums and water beds. Some don't even allow them!
Zorfox is offline  
post #14 of 17 (permalink) Old 11-06-2015, 07:02 PM
Planted Tank Guru
 
PlantedRich's Avatar
 
PTrader: (2/100%)
Join Date: Jul 2010
Location: United States
Posts: 12,121
This seems to be one of the areas where the specs and the real world may not fit too well. Just for grins, I did a little looking at some numbers.
I think we can all agree that a floor should not strain to hold up a normal refrigerator? So let's do some math.
I took 30" by 30" as a normal size and a quick search says 300 is a "normal" weight.

2.5' X 2.5= 6.25 Sq Ft. so using the 40PSF figure gives us a safe weight of 250 pounds

So using the specs, does the frig drop through a new wood floor if we add a 100 pounds of frozen food? I'm gonna be watching who I set next to at Thankgiving this year!!! I have a couple friends who shake the ground when they walk but I never worried about them crushing the building.
PlantedRich is offline  
post #15 of 17 (permalink) Old 11-06-2015, 09:06 PM
Wannabe Guru
 
lksdrinker's Avatar
 
PTrader: (9/100%)
Join Date: Feb 2014
Location: NY; LETS GO METS
Posts: 1,916
Quote:
Originally Posted by PlantedRich View Post
This seems to be one of the areas where the specs and the real world may not fit too well. Just for grins, I did a little looking at some numbers.
I think we can all agree that a floor should not strain to hold up a normal refrigerator? So let's do some math.
I took 30" by 30" as a normal size and a quick search says 300 is a "normal" weight.

2.5' X 2.5= 6.25 Sq Ft. so using the 40PSF figure gives us a safe weight of 250 pounds

So using the specs, does the frig drop through a new wood floor if we add a 100 pounds of frozen food? I'm gonna be watching who I set next to at Thankgiving this year!!! I have a couple friends who shake the ground when they walk but I never worried about them crushing the building.
Valid point about the fridge. But one thing to keep in mind is that the placement of those kinds of appliances are usually pre-planned and a builder might reinforce certain areas of the floor in these specific locations. Especially if corners are being cut elsewhere! But I guess this comes more into play in older wooden home construction. Areas where more weight was to be expected (bathtubs usually) would often get some beefing up of the floor in that spot.

Rich's Fishes
Curator of an ever growing fishroom that currently houses 30 different tanks. Most full of at least water....some even have fish!
lksdrinker is offline  
Reply

Tags
None

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the The Planted Tank Forum forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome