How tight should a threaded PVC fitting be?


Does anyone know officially (for example as per the plumbing code) how tight a threaded PVC fitting should be? I'm guessing it's hand tighten + X number of turns.

Thanks,
Harry
Harry Muscle is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 10-07-2009, 03:30 PM   #2
Postal Penguin
Planted Tank Obsessed
 
PTrader: (6/100%)
Join Date: Mar 2009
Location: CO
Posts: 414
Default

I dont know the code but I use teflon tape and a wrench.
Postal Penguin is offline   Reply With Quote
Old 10-07-2009, 03:58 PM   #3
Regloh
Algae Farmer
 
PTrader: (8/100%)
Join Date: Jan 2009
Location: Medford, MA
Posts: 683
Default

I have no idea what the torque spec on these is, or if it's even specified like that. But I have seen instructions that say "turn until it doesn't leak anymore". You do not want to over tighten a pipe thread...
__________________
Eheim Pimp #363 - 2213, 2217

Tank journals: 55g, 10g
Regloh is offline   Reply With Quote
Old 10-07-2009, 05:36 PM   #4
Hoppy
Planted Tank Guru
 
Hoppy's Avatar
 
PTrader: (74/100%)
Join Date: Dec 2005
Location: Sacramento, CA
Posts: 18,659
Default

Teflon tape isn't a good idea on PVC threaded fittings, according to the fitting manufacturers. The primary purpose of teflon tape is to lubricate the treads so the fitting can tighten further with less effort, and that leads to breaking the PVC female fittings. Instead, the use of thread joint compound, a paste, which is made for use on PVC pipe, is recommended. Then notice that most PVC pipe thread connections don't have wrench flats or they have minimal wrench flats. That means they are not intended to be tightened with crescent wrenches, for example. Instead, tighten them by hand, plus a little with a wrench or adjustable pliers (not recommended by the manufacturers, but it works.) You have to get a feel for what the right torque is, judging by what you have found makes a non-leaking connection. It doesn't take long to learn what too much torque is, but the fittings are cheap, so replacing the broken ones isn't that big a deal.
__________________
Hoppy
Hoppy is offline   Reply With Quote
Old 10-07-2009, 06:33 PM   #5
Wicket_lfe
Planted Tank Enthusiast
 
PTrader: (7/100%)
Join Date: Aug 2008
Location: Long Island and Queens
Posts: 860
Send a message via AIM to Wicket_lfe
Default

yea my basic rules, as i stand in the aisles of Home Depot, is just buy 3 of every fitting. One to break, one to test, and one to hopefully finally work. haha.
Wicket_lfe is offline   Reply With Quote
Old 10-07-2009, 10:12 PM   #6
PDX-PLT
Planted Member
 
PTrader: (0/0%)
Join Date: Feb 2007
Location: NW Oregon
Posts: 292
Default

Quote:
Originally Posted by Hoppy View Post
Teflon tape isn't a good idea on PVC threaded fittings, according to the fitting manufacturers. The primary purpose of teflon tape is to lubricate the treads so the fitting can tighten further with less effort, and that leads to breaking the PVC female fittings. Instead, the use of thread joint compound, a paste, which is made for use on PVC pipe, is recommended.
That's correct.

You have to be especially careful with female PVC fittings. Since U.S. pipe fittings are tapered, the male fitting can act like a wedge, and split the female fitting. BTDT.

As a general rule, I never use a metal male fitting with a PVC female fitting, and like to avoid PVC female fittings. When I do use one (with a plastic male fitting), I use paste, and about one turn past hand-tight.
PDX-PLT is offline   Reply With Quote
Old 10-07-2009, 11:11 PM   #7
PMaj
Algae Grower
 
PTrader: (4/100%)
Join Date: Dec 2006
Location: Fremont< CA
Posts: 23
Default

Hoppy is right. It just has to be water tight. With 'pipe dope' you can get this. You also have to remember that you're working with maybe a 10 lbs. psi max with pumps, filters,etc.
Pat
PMaj is offline   Reply With Quote
Old 10-08-2009, 04:02 PM   #8
BG1772
Algae Grower
 
PTrader: (1/100%)
Join Date: Jul 2009
Location: Columbus, Ohio
Posts: 46
Default

Also, the fittings use National Pipe Thread standard. This thread type tapers, so that the joint gets tighter the more revolutions. It should not require more than a 1/4 to 1/2 turn past the hand tight point to seal a pipe for aquarium use.

EDIT -- I found this on LASCOs site. They say no more than 2 turns past finger tight.

http://www.lascofittings.com/support...dedPlastic.asp

Last edited by BG1772; 10-08-2009 at 04:09 PM.. Reason: more information
BG1772 is online now   Reply With Quote
Old 10-08-2009, 04:33 PM   #9
Harry Muscle
Planted Member
 
Harry Muscle's Avatar
 
PTrader: (1/100%)
Join Date: Mar 2007
Location: Canada
Posts: 275
Default

Quote:
Originally Posted by BG1772 View Post
Also, the fittings use National Pipe Thread standard. This thread type tapers, so that the joint gets tighter the more revolutions. It should not require more than a 1/4 to 1/2 turn past the hand tight point to seal a pipe for aquarium use.

EDIT -- I found this on LASCOs site. They say no more than 2 turns past finger tight.

http://www.lascofittings.com/support...dedPlastic.asp
Very interesting link.

Thanks,
Harry
Harry Muscle is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT. The time now is 02:04 PM.


Powered by vBulletin®
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Copyright Planted Tank LLC 2012