SOLVED: CyberPower UPS + Rena XP3 (XP-L) = No Good?
I have two CyberPower 1500AVR UPSs that I use for computers.
I just hooked my aquarium equipment (2x Rena XP3) into one of the UPS and decided to do a power outage test and was very disappointed. When I unplug the UPS power cord from the wall outlet it switched to a battery backup and both filters started making ‘scratching’ noise and the outflow was down to almost 0. I tried the second CyberPower UPS – same results. I’m glad I tested this now… Are CyberPower UPSs not good for this kind of application? SOLVED: Rena XP3s are working fine with CyberPower PFC compatible Pure sine wave (PFCLCD) UPS! Last edited by Bubba_Shrimp; 01-23-2013 at 10:21 PM.. Reason: Problem solved |
|
|
|
| Sponsored Links | |||
Advertisement | |||
|
|
#2 |
|
Planted Tank Obsessed
|
Just tested Rena XP3 with an old APC ES 725 - same problem. What the heck?
|
|
|
|
|
|
#3 |
|
Planted Member
|
Oh man I remember back in my reefing days hearing that battery backups are not good for aquarium equipment... I am trying to remember why for the life of me, has something to do with the way the battery delivers the power or something. I'll do a little research, see what I can find.
-Scott |
|
|
|
|
|
#4 | |
|
Planted Tank Obsessed
|
Quote:
|
|
|
|
|
|
|
#5 |
|
The Security Dude
|
You need to make sure they are line interactive ups. I use them and have some alpha tech battery back ups for my tanks and they last about 45 min. I am about to buy a generator
Sent from my iPad 3 using Tapatalk HD
__________________
55 Planted Rummys,2 GBR,8 Corys,4 Discus PFR Culls
Many shrimp tanks http://www.plantedtank.net/forums/sh...half-done.html |
|
|
|
|
|
#6 | |
|
Planted Member
|
Quote:
"Being an Electrical Engineer, I know that most battery backup systems that you can buy in your local Wal-Mart or Target stores (APC comes to mind) that are strictly battery backup will provide essentially a square wave output when operating (versus a sine wave from the power company), and most pump equipment could potentially be damaged under such a power source - they're just not designed to operate on that type of power. So I would think that at most, you would just want to select one power head to put on battery backup and make sure you have enough established Live Rock in the system to support biological conversion during an outage." This isn't my knowledge, just someone else who has a much better understanding lol. They further went on to say: "If you wanted to run the main pump off a backup system, I would think the ONLY way to do it would be to do it right, and buy a "True" Online Double-Conversion UPS. This device takes the input from the power company, converts it to DC, then back to AC to the equipment it supplies power to. The batteries are charged on the DC side. This type of unit provides a nice clean sine wave (it also cleans up the utility power signal so you will extend the life of your equipment) but it also costs quite a bit - usually $300 to $500. You will usually get longer running time also, since these are designed to keep a larger piece of equipment running, such as a computer server long enough to keep the system running during a short-term outage, and with enough time to perform a proper system shut-down once the batteries start to run out." Hope any of that helps -Scott |
|
|
|
|
|
|
#7 |
|
Planted Tank Obsessed
|
This is from my CyberPower 1500AVR description: "Line interactive, AVR and GreenPower Corrects brownouts and overvoltage without using the battery. GreenPower UPS reduces energy consumption up to 75%".
|
|
|
|
|
|
#8 |
|
Planted Member
|
Yep, square wave and these magnet motors don't get along well.
__________________
72 Bow, Finnex Ray 2 LED Light, Pressurized CO2, GLA Inline Atomic Diffuser, Eheim Ecco Pro 2236, (2) Koralia Nano 240s
BriDroid on APC & APE k20z3 on DFWFishBox Brian in Real Life |
|
|
|
|
|
#9 |
|
Planted Tank Obsessed
|
Will this work then?
http://www.amazon.com/CyberPower-CP1.../dp/B00429N19W |
|
|
|
|
|
#10 |
|
Planted Member
|
That looks like it would fit the bill. Indicated it does change it back to AC power before sending it to the equipment. I personally don't have the electrical engineering background to say from my own knowledge that it will work, but it seems to me that it matches the description of the person I quoted.
|
|
|
|
|
|
#11 |
|
aka Nick
|
I don't think that's what you want. According to the description you want Online Double-Conversion UPS.
http://cyberpower.advizia.com/CyberP...CyberPower_UPS
__________________
|
|
|
|
|
|
#12 |
|
Planted Tank Obsessed
|
Anybody has $600 laying around for me to test it out?
Darn, these things are expensive... How do hobbyists go around the backup power problem for their filters/pumps? |
|
|
|
|
|
#13 |
|
aka Nick
|
I think most would have a back-up generator. If you have enough money to invest in a large high-tech reef or even discus tank you most likely have enough money to install a generator.
UPS aren't going to last for a long power outage anyways.
__________________
|
|
|
|
|
|
#14 |
|
Planted Tank Obsessed
|
Which generator would you recommend? I see gas/gasoline/diesel powered... tons of options out there.
|
|
|
|
|
|
#15 |
|
Planted Member
|
I'd go for a plain gas generator, so long as you have an outdoor space for it to sit, and enough gas, you could keep your tank running indefinitely when the power goes out.
Only issue with a generator is that even when not in use, they have to be serviced regularly, otherwise they are likely to not work when you need them. -Scott |
|
|
|
![]() |