#31 (permalink) |
|
Algae Grower
|
Homage to a great DIY, thanks Wasserpest for bringing it to the masses.
I refitted a rack mounted power strip with relays to get a nicer look. $35 on top of Wasserpests estimate. Note to everybody thinking about this, BUY 24 VAC relays not DC relay. DC relays will make a funny noise while switching
|
|
|
|
|
|
#37 (permalink) |
|
Grow Baby Grow
|
I was doing some research and stumbled across this (very nice) setup. I was going to do something similar using a PLC that I have kicking around, but after seeing your set up I am favoring your relay logic vs. my PLC.
I understand the whole system is protected by whatever outlet you house is rated for, for example you most likely on a 20A or 30A house circuit breaker. But what are you’re thought on protecting the main 120V coming to the outlets with a fuse or protecting each branch with their own fuse? I might be over thinking the set up or I just might be over paranoid, but just wanted to get some thoughts and make sure I don’t’ burn down the house. |
|
|
|
|
|
#38 (permalink) |
|
Born to be mild
|
I hope the regular circuit breaker is sufficient. Rather than using circuit breakers for each outlet, I would consider to upgrade the relay wiring. Maybe find relay sockets with more secure connections... soldering directly to the relay pins isn't the the best solution.
The whole thing is plugged into a GFCI protected outlet. Separate circuits might be good for reef tanks with lots of metal halides and big pumps, my 100gal setup draws less than 300W, plus another 200W (rarely) when the heater kicks in. |
|
|
|
|
|
#39 (permalink) | |
|
Algae Grower
|
Quote:
You can get relay sockets the same place you get the relays providing they are not PCB mount Keep it up and great job!!!
__________________
V P #8
Me, no Iphone nope not I. Heck I would not even have a cell if I was not married. |
|
|
|
|
|
|
#40 (permalink) |
|
Newbie
|
I consider application of the Wasser-Controller for dosing with SP100 peristaltic pumps. My plan is to convert 24VAC control signal into DC driving SP101.051 pump.
According to the SP 101 spec sheet SP101.051 draws upto 75ma @24VDC and pumps about 2.1 ml/min. 8006 irrigation controller supplies 24 VAC, 0.27 amps per station, which should be sufficient to drive SP100. What do you guys think? Will this work? How would I convert 24VAC to 24VDC? |
|
|
|
|
|
#41 (permalink) |
|
Planted Member
|
Anyone know of a different controller that will work like the DIG 8006? I think it needs to be a drip irrigation timer (longer times and should be able to overlap zones), but I'm not finding anything out there.
Just hoping someone have found something that will work. thanks, dave |
|
|
|
|
|
#42 (permalink) |
|
Born to be mild
|
When I originally researched this, I checked the other commonly used brands (Rainbird, Orbit) and they didn't have anything that combined everything needed to make it work. I was about to throw in the towel, when I came across the DIG.
I believe they are still sold here. If you'd like I can check the price and send it to you for that plus shipping. You could also check w/ Glenn (gmccreedy) to see if he has one for sale, not sure. |
|
|
|
|
|
#45 (permalink) | |
|
Algae Grower
|
Quote:
|
|
|
|
|
![]() |